In a three-phase system, what voltage is measured between secondaries?

Study for Con Edison Test B – Gas Safety, Electrical Theory, and Job Procedures. Prepare with multiple choice questions, each with hints and explanations. Get ready for your exam!

Multiple Choice

In a three-phase system, what voltage is measured between secondaries?

Explanation:
In a 120/208 V three-phase system arranged in a wye, each phase to neutral is 120 V, and the voltage between any two phases (between two secondaries) is the line‑to‑line value. The line-to-line voltage in a wye system is the phase voltage multiplied by the square root of 3: V_LL = √3 × 120 V ≈ 208 V. So measuring between two secondaries yields about 208 V. The 120 V value would be from a single secondary to neutral, not between secondaries. The 277 V value is the line-to-neutral voltage for a 480Y/277 V system (not applicable here), and 69 kV is a high transmission voltage, not a typical secondary in this context.

In a 120/208 V three-phase system arranged in a wye, each phase to neutral is 120 V, and the voltage between any two phases (between two secondaries) is the line‑to‑line value. The line-to-line voltage in a wye system is the phase voltage multiplied by the square root of 3: V_LL = √3 × 120 V ≈ 208 V. So measuring between two secondaries yields about 208 V.

The 120 V value would be from a single secondary to neutral, not between secondaries. The 277 V value is the line-to-neutral voltage for a 480Y/277 V system (not applicable here), and 69 kV is a high transmission voltage, not a typical secondary in this context.